Wiki How To forum


Welcome to the Wiki How Forum forums.

You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.
Go Back   Wiki How Forum > Home improvement > Electrical
Reply
 
LinkBack Thread Tools Display Modes
  (#1 (permalink)) Old
Junior Member
 
Default About Generator as sole power source - 03-27-2008, 02:27 PM

This is a three part question really, and I apologize if it has already been answered but I am really drawing a blank on this one.

I have built a cabin that will be powered only by a generator. There is no, and will be no grid power, unless of course I hit the lottery. I have five 20a circuits and plan to wire them to a panel directly. I have a Honda 3000w generator with a max output of 30a at 120v. (I overwired the circuits just to plan for that lottery jackpot) Here are my questions.

1. I will hardwire the breaker panel to an outlet on the outside of the cabin. The total length of that feed wire, by the time I string it through the walls, will be approximately 40 ft. What size wire will that feeder wire need to be? #8?

2. In time I intend to build a small storage shed near the cabin and eventually locate the generator next to the shed. When I do this I will bury the wire from the cabin ( at the point that the outlet will be located) to the shed. I anticipate the total length of that wire to be approximately 40 feet, for a total feed wire length of about 80 feet from generator to the panel. Am I still OK with a #8 wire, using approved wire for direct bury, for a length of 80 ft total? Do I need to go to a #6 because of the distance?

3. How do I ground this system? Do I ground the system at the outlet on the outside of the cabin with a driven ground rod, and then later disconnect that rod and drive another one at the location of the generator in the shed?

Any help would be greatly appreciated!!!!
   
Reply With Quote
  (#2 (permalink)) Old
Junior Member
 
Default 03-27-2008, 02:28 PM

I actually am unable to definitively answer questions 1. & 2 because I'm only familiar with Australian electrical regulations. With regard to your third question, in Australia it is illegal to ground (earth) a generator unless it is done so in a dedicated generator switchboard & only if the generator has a provision for being earthed. Something tells me that the rules for this are different in the USA.

I also think you may like to check the sizing of your generator. I have prepared an example of sizing (for single phase 120 volts) as follows;

Continuous Load calculation.
4 x 60 Watt incandescent lights - - - - - - - - - - 240 divided by 120 = 2 Amps.
1 x 300 Watt fridge - - - - - - - - - - - - - - - - - - - 300 divided by (120 x 0.8) = 3.125 Amps.
1 x 300 Watt freezer - - - - - - - - - - - - - - - - - - 300 divided by (120 x 0.8) = 3.125 Amps.
1 x 300 Watt TV - - - - - - - - - - - - - - - - - - - - - 300 divided by 120 = 2.5 Amps.
1 x 100W "printer" fax/phone - - - - - - - - - - - - 100 divided by 120 = 0.8 Amps.

Total continuous Watts as listed - 1240 Watts.
Total continuous current as calculated - approx 11.55 Amps.

Surge Load calculation.
The only items that will have a surge current are the fridge, freezer & TV.

1 x 300 Watt fridge - - - - - - - - - 3.125 Amps x 4 = 12.5 Amps.
Fridge surge - - - - - - - - - - - - - - 12.5 Amps - 3.12.5 Amps = 9.375 Amps.

1 x 300 Watt freezer - - - - - - - - 3.125 Amps x 4 = 12.5 Amps.
Freezer surge - - - - - - - - - - - - - 12.5 Amps - 3.125 Amps = 9.375 Amps.

1 x 300 Watt TV - - - - - - - - - - - TV surge is approx 1 Amps.

Total surge current - 19.75 Amps.

Your generator will need to supply a continuous current of 11.55 Amps (12 Amps).
Your generator will need to supply a total surge current of 11.55 Amps + 19.75 Amps = 31.3 Amps.
Converting these figures to "Apparent Power" (VA);
31.3 Amps x 120v = 3 756 VA surge.
11.55 Amps x 120v = 1 386 VA continuous.

Since you will not find a generator with these exact "continuous" & "surge" ratings, you must buy a generator that can accommodate the surge rating. ie you will need a generator with a surge rating of no less than 3 760 VA for the above situation.

Also, most "portable" generators have a duty cycle, whereby it can only operate at full load for a maximum period of time. If this operation time is exceeded, the life of the generator can be dramatically reduced. Generally, reduced loads mean a longer operating time.

Unless your "portable" generator has inverter technology, it may produce a waveform that can be detrimental to certain equipment.

In your situation, "standby" generators are used because they are designed to operate continuously & they also provide a "clean" output waveform.
   
Reply With Quote
  (#3 (permalink)) Old
Junior Member
 
Default assets of - 08-16-2008, 08:36 AM

Happening Filmmaker sucks. What sucks fastened solon is in my region their instalment is Utili-Comm Southwestern, Which I'm pretty measured is owned by Beelzebub himself.Throttling WoW interaction would be pretty Lineage2 adena It doesn't use untold bandwidth at all. (And if you dubiety that, conceptualise that the 1000 to 3000 players that strength be on a machine at one acknowledged statement add up to an assets of bandwidth that the server can dealing with, and then nonentity.
   
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On




Powered by vBulletin® Version 3.6.8
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
vBulletin Skin developed by: vBStyles.com